Overslaan naar hoofdinhoud
Winkelwagen

Concrete breakout from two different beams

Geplaatst door Monika Petkovskaalmost 2 years ago
Concrete breakout from two different beams

I have two steel beams connecting on one concrete column.
How can I take into consideration the effect on the concrete from the two forces from each beam.

anchor,concrete cone

1 Antwoord
Geplaatst door Belux engineeringalmost 2 years ago
Geverifieerd door Hilti

You will need to split the post in two and ensure that half of the thickness is at least equal to the minimum embedment depth (hmin) required for the anchor. The hmin value depends on both the rod diameter and the embedment depth. After that, you will need to perform two separate calculations.However, please note that the column may be too narrow for this configuration depending on the loads.

anchor,concrete cone