Overslaan naar hoofdinhoud
Winkelwagen

Reinforcement - anchorage in concrete

Geplaatst door Eline Vanthournoutalmost 4 years ago
Reinforcement - anchorage in concrete

Hi, I would like to add reinforcement in the concrete foundation block but I get a warning that it is not possible: "Additional reinforcement is only possible for static and seismic anchorages up to 9 anchors and with EN1992-4. I have a static calculation and only 4 anchors an EN1992-4 is chosen. Why do I get this message?

additional reinforcement,anchorage concrete

2 Antwoorden
Geplaatst door Hilti Belux Engineering Teamalmost 4 years ago
Geverifieerd door Hilti

Dear Eline,

Thank you for the question! Could you transfer us the .pe file by email on belux.engineering@hilti.com? I'm not able to open the file you attached here.

Kind regards,
Belux Engineering Team


Geplaatst door Hilti Belux Engineering Teamalmost 4 years ago
Geverifieerd door Hilti

Dear Eline,

Thank you for your question.

As you see you will get the following notification:


And indeed you selected the design method EN 1992-4 based:


But at this point your configuration of the anchors is not confirm on the design method EN 1992-4. There are only some specific configurations that are confirm to the EN 1992-4. Below you can find what they are:


If your anchor configuration is not following one of the layouts above, you're not following the EN1992-4 as the notification says. And at this point it's not possible to add supplementary reinforcement in Profis Engineering.

Sorry for the inconvenience and I hope this answer helped you?

Kind regards,
Belux Engineering Team

Profis Engineering,EN1992-4,design method,supplementary reinforcement